    Foundation Plugin
    451 Posts 15 Posters 580.3k Views 15 Watching
    • medeekM Offline
      medeek
      Any thoughts on an advanced option that auto-inserts anchor bolts?
      https://3dwarehouse.sketchup.com/warehouse/getpubliccontent?contentId=23b772c0-6d89-43a2-8fd7-b630eb323bf5
      Options would be:
      Size: 10", 12", 14"
      Dia.: 1/2", 5/8"
      Washer: 3"x3" Square, 2"x2" Square, Round
      O/C Spacing (ft.): 6'
      Sill Plate Thickness (in.): 1.5"
      Distance from Corners (in.): 12"
      Nathaniel P. Wilkerson PE
      Medeek Engineering Inc
      design.medeek.com
      • medeekM Offline
        medeek
        The argument for this construction method is the sheathing height is decreased because the rim board is eliminated. However, in my mind the cons outweigh the pros:
        1.) There is a thermal bridge through the stemwall at the corner where the floor meets the wall.
        2.) Stemwall construction would become more complicated and time consuming.
        3.) Proximity of the I-Joist to the concrete could be problematic, requiring additional measures and more time and effort.
        4.) The crawspace height is reduced making it harder for other subs to install and work in and moisture from the ground is more likely to be an issue.
        5.) Nut and Washer of anchor bolts protrudes into floor sheathing and bottom wall plate, requiring additional notching.
        6.) If you want to run plumbing or electrical down through the wall bottom plate and into the floor, this is nearly impossible with this configuration.
        design.medeek.com
        • pbacotP Offline
          Those are all good points. We use a similar method but use a single ledge. It's useful if you want the exterior concrete to come up higher due to clearance at grade or terraces alongside the wall. Sometimes there might be additional concrete wall as a sort of curb higher than the floor. You still have to make the min. crawl space clearance. Yes more hassles for plumbing and electrical. Nice option on adding anchor bolts.
          • medeekM Offline
            medeek
            I'm trying to determine if its easier to write a module that draws the anchor bolts or just bring in the component (pre-drawn). I've never brought in a component before so something I need to explore further. The other thing I feel is key is to make sure any of these minor components are modeled in such as way as to remain fairly lightweight within the model. No one is going to want to use a feature that bogs down their overall model. That is my one big gripe with using the 3D Warehouse models, the polygon count on most models is usually outrageous.
            design.medeek.com
            • medeekM Offline
              medeek
              I need some input from the foundation and truss plugin users. I've decided to pre-model certain things like Bolts, Nuts, Washers etc... With Nuts and Bolts I'm planning on using a cosmetic thread so that the polygon count is minimal. As I've been experimenting with the bolts and nuts I'm wondering if I should eliminate the 30 deg. bevel on the head of the bolt and nut, it looks nice but adds quite a bit of complexity and polygons to the model. Any thoughts on this?
              You would sacrifice some realism for a smaller model...
              design.medeek.com
              • facerF Offline
                facer
                The question arises as to what will be THE INTENDED PLUGIN USE by the majority of users?
                Foundation detail requiring a Realistic look for "bolts" in construction details is not high on my list.
                The hierarchy of detail will depend on the "scale of detail".
                I would suggest users be given the following options that allow a selection:
                1. No bolts to be shown
                2. Simple bolts without bevel
                3. Detailed bolts showing bevel.
                Hope this helps?
                • jujuJ Offline
                  juju
                  Simple bolts. More detailed will only be required in detailing, which generally are separate (highly detailed) models.
                  • medeekM Offline
                    medeek
                    For now I will eliminate the beveling of bolt heads and nuts, the added number of polygons is too hard to justify and the bevel doesn't really add much when your zoomed out at building scale anyways (in other words you really can't see the bevel).
                    There is always an option to turn the anchor bolts on or off, that is a given. Some users may want this function others may have absolutely no use for it. It will be there if you need and want it.
                    For now I am going to go with 1/2" and 5/8" anchor bolts, I can always add more sizes later by request. The standard sizes of anchor bolts are per a specification I pulled from Fastenal (major manufacturer of fasteners in the US). I will start with 10", 12" and 14" lengths.
                    For the square washers I will give an option between 2"x2" and 3"x3", with the 3x3 being the more typical I would think with the latest 2012 and 2015 cycle of ICC codes. The exact dimensions of the square washers are per Simpson Strong-Tie's offering in there wood fastener manual.
                    The hex nuts are per the Machinery Handbook 27th Edition.
                    If anyone has a metric spec. for anchor bolts (L-bolts) please send it my way and I can add in the metric equivalents.
                    design.medeek.com
                    • pbacotP Offline
                      I'd say for an overall building model-- as long as part is recognizable, dispense with the niceties to save poly count. Not sure how the intent of the model would be. Does anyone really expect to cut details from the overall model?. Personally a foundation model with AB and all would be specialty one-off image, so that a builder can look at either a 3d image or the SU model to visualize a complex foundation. Other than that, the real information is in a foundation plan with standard and custom details.. all full of text and dimensions and tables all 2d, and really having little to do with a full building model in SketchUp. I've yet to have much interest from others in the foundation model idea, as ultimately they must build from a set of 2d plans. I have to say the work here is impressive. I doubt however the parametric results would be that close to what our plans actually come out to representing. Many designs, when it comes to foundation anchors and holdowns are inch by inch worked out--and even then we don't illustrate every standard requirement, for example the extra bolts needed for a plate splice. Or the AB might not be shown at all since they have to be laid out by the builder based on several details and requirements.
                      • medeekM Offline
                        medeek
                        I think the intent with providing the anchor bolts is partly a graphical representation and also for estimating. Ultimately the exact layout of the sill plates will drive the number and location of the anchor bolts as well as any requirements from an engineer for tightening up the spacing due to lateral loads and shearwalls.
                        Per the code (IRC/IBC) you are required to have at least two (2) anchor bolts per sill plate segment and the bolts must be within 12" of the end of the segment and no closer than 7 bolt diameters (3.5" for a 1/2" DIA bolt). Max. spacing is 6' o/c with 7" min. embedded.
                        So even if I lay out my bolts starting 12" from the edge of the foundation and space them at 6' o/c there will probably still be some additional bolts required since there will be sill plate splices (for buildings larger than 16'x16').
                        I've always wondered if the builders actually give this much thought as they are placing their anchor bolts.
                        Another question I have is one would not want the anchor bolts to clash with the Floor Joists or Trusses. Do the contractors typically layout the location of the anchor bolts to ensure that this does not happen.
                        Your right there are a lot of constraints on the location of the anchor bolts, hence it actually might be useful to a designer to have them in the model to see potential issues as those raised above.
                        design.medeek.com
                        • medeekM Offline
                          medeek
                          This brings to mind something I saw on a construction site a couple years ago. A contractor was framing up a garage wall and one of the anchor bolts landed exactly in the middle of one of the wall studs. A big V-shaped notched was removed from the bottom of the stud, to the point that the bearing strength of that stud was severely compromised. A 3.5" sill plate also leads to situations like this:
                          http://www.icreatables.com/images/framingimgs/framing-floor/rim-joist.jpg
                          design.medeek.com
                          • pbacotP Offline
                            If there's a rim jst., don't use a 2x4 plate. Some builders, I am sure, work out a lot of this beforehand, especially if the general is also the framer. And in some other jobs such coordination may be impossible. If the bolt lands on a stud, I suppose extra studs can be added and the stud needed for attachment can be headed off at the bolt. Now some mechanically fastened bolts are approved for anchor bolts. Some innovation in technology is in order to be sure.
                            • medeekM Offline
                              medeek
                              The 1/2" and 5/8" anchor bolts, washers and some standard nuts.
                              https://3dwarehouse.sketchup.com/warehouse/getpubliccontent?contentId=471d6963-9bbc-410e-b78b-b613db0fd3f7
                              View models here:
                              3D Warehouse
                              (3dwarehouse.sketchup.com)
                              design.medeek.com
                              • medeekM Offline
                                medeek
                                Version 1.0.7 - 03.19.2017
                                • Added 1/2" and 5/8" Dia. Anchor Bolt option to stemwall and slab on grade foundations.
                                • Anchor bolt lengths are nominal 10", 12" and 14", square washers are 2"x2" or 3"x3".
                                http://design.medeek.com/resources/images/foundation_su22_800.jpg
                                View model here:
                                3D Warehouse
                                The anchor bolt, washer and nut are three separate files that are loaded in as components. Then the nut and washer components are inserted inside the bolt component and exploded so only the solid group(s) remain. Its pretty amazing what you can do with a robust API and a little bit of Ruby code.
                                It took me most of today to figure out how to do all of this since I'm in uncharted territory but now that I've got it kind of figured out it opens up the possibility for a host of other things (holdowns, windows, doors, vents etc...) for this plugin and the others I'm working on.
                                design.medeek.com
                                • medeekM Offline
                                  medeek
                                  The cosmetic threads actually render quite nicely as does my rebar material/texture. I just realized I have not added any custom materials into the foundation plugin.
                                  http://design.medeek.com/resources/images/foundation_su23_800.jpg
                                  As you can see from the image the orientation of the J-bolts is the same regardless of the wall, however it would not be a couple more lines of code to orient them all facing in or facing out or some other combination. Curious how the contractors actually install these, is the orientation important?
                                  I tried to put the 25 degree incline on the rebar grooves but there are some difficulties with extruded circular shapes and materials so the best I can do is the concentric rings as shown.
                                  design.medeek.com
                                  • facerF Offline
                                    facer
                                    Orientation of J-bolts
                                    I would think parallel to the wall to give maximum concrete cover
                                    surrounding the J-bolt ends.
                                    • medeekM Offline
                                      medeek
                                      I've been talking to a few other contractors out there and most of them don't pay alot of attention to the orientation of the J-bolts into the concrete, they let the concrete set up a bit and then stab them in.
                                      I'm adding in the custom materials, stemwall foundation below is an example:
                                      http://design.medeek.com/resources/images/foundation_su24_800.jpg
                                      I will need to roll another revision probably tomorrow to get this update out there.
                                      I was wondering about adding in the option for vents in the stemwall, for foundations with crawlspaces. Any thoughts on this and what is standard construction in your locale as well as what type/brand of foundation vents/inserts are used.
                                      design.medeek.com
                                      • medeekM Offline
                                        medeek
                                        The ICC codes call out a minimum of a one vent within 3 feet of each corner. It shouldn't be to much trouble to create the openings in the stemwall and place some vents:
                                        http://design.medeek.com/resources/images/foundation_su25_800.jpg
                                        For a rectangular building (4 sides) should I place 4 vents or 8 vents? Provide only the openings or also provide a generic foundation vent (lightweight geometry?)
                                        Moving an opening is actually very easy within SketchUp, when it comes to a solid wall like this.
                                        What is the typical header thickness between the top of the vent hole and the top of foundation?
                                        Vent size seems to be 16"x8" for most vents I've seen.
                                        With regards to vents there are the cheap plastic ones you can get a Home Depot or Lowes and and then there are a whole ton of more expensive louvered metal manufacturers of vents and flood vents.
                                        design.medeek.com
                                        • medeekM Offline
                                          medeek
                                          I've been slowly plugging away at the polygon stemwall tool, but as I was driving to work this morning I realized it would also be useful to have a simple linear or line tool as well for creating straight segments.
                                          design.medeek.com
                                            MtnArch
                                            What I usually do is provide a solid wood header within the floor framing and suck the vents up tight to the top of the stem wall.
                                            As to size, it will vary depending on the topography of the site, total size of the underfloor area, etc. Also, here in California if you are in the "SRA" (State Responsibility Area, which is where fire protection is provided by state forces such as Cal Fire) you have to use approved ember-resistant vents which are further limiting.
                                            Highest Regards,
                                            Alan T. Hendry, RA
                                            Architect
                                            • 22
                                            • 23
                                            • 4 / 23
