    Medeek Wall Plugin
    1.6k Posts 29 Posters 2.2m Views 28 Watching
    • medeekM
      medeek
      @pbacot said:
      Impressive! Do you end up with a list of shear walls and identification by type and length?
      That would be the next step.
      It would be nice if there was a function which created a Shearwall schedule, like I make on my own structural sheets.
      Nathaniel P. Wilkerson PE
      Medeek Engineering Inc
      design.medeek.com
      • medeekM
        medeek
        Working on the shearwall (panel) anchor bolts and sole plate fasteners.
        First look at some anchor bolts associated with a shear wall:
        https://aws1.discourse-cdn.com/sketchup/original/3X/f/3/f30e60bd116a04602cc53e23d7904d1dae1fb28b.jpeg
        When a shearwall rests directly on a slab-on-grade then the anchor bolts are typically connected directly to the sole plate of the shearwall, however when the wall rests on a floor as shown then the anchor bolts will anchor the sill plate below the wall and threaded rods with coupler nuts are utilized to extend the holdown bolts up to the HDU holdowns. In this situation the engineer will also typically call out the size and spacing of fasteners that connect the sole plate of the shearwall to the rim joist below it.
        To facilitate various wall/floor configurations the vertical and horizontal offset parameters for shearwall anchor bolts are made available for each shearwall, and can be adjusted independently.
        P.S.
        Looking at this image it immediately jumps out at me that a critical component within this shearwall assembly is missing. Note that I am not showing fasteners, they are too small to model for the most part. Let's see if anyone can pick it out.
        design.medeek.com
        • medeekM
          medeek
          Version 1.7.7b - 12.28.2020
          • Enabled anchor bolts within the shearwall module.
          • Enabled sole plate fasteners within the shearwall module.
          • Enabled top plate clips within the shearwall module.
          http://design.medeek.com/resources/wallplugin/images/wall_su446_800.jpg
          http://design.medeek.com/resources/wallplugin/images/wall_su447_800.jpg
          http://design.medeek.com/resources/wallplugin/images/wall_su448_800.jpg
          All that is left is the specialized blocking for shearwalls.
          design.medeek.com
          • medeekM
            medeek
            I've seen both ways of handling stacked shearwall panels, however the strap method would make more sense from an economic standpoint:
            https://aws1.discourse-cdn.com/sketchup/original/3X/3/5/35940ec6ad50fbde3f147a4a5e261f3640b664f4.jpeg
            https://aws1.discourse-cdn.com/sketchup/original/3X/9/0/903ab00c8c1ee58b46a194826563a16c0c163fec.jpeg
            The main point here is that you have either option at your disposal with the new shearwall module.
            Notice the inclusion of the top plate clips on the lower shearwall and the 16d Common fasteners in the sole plate of the upper shearwall. Both of these items are optional however if that degree of detail is required or desired it is also readily available to the designer or engineer.
            See model here:
            3D Warehouse
            (3dwarehouse.sketchup.com)
            P.S.
            Some of you may be scratching your head looking at all of this hardware that goes into a wall especially at a shear panel... I know, Simpson Strong-Tie isn't a multi-million dollar company for nothing. A lot of old time contractors really dislike us engineers.
            Bottom line, when the wind blows really hard or you just happen to be lucky enough to be in a major earthquake, these construction methods will prevent your house from toppling over and potentially killing you.
            Engineers like myself are entrusted with making sure the built environment around you is safe and secure.
            design.medeek.com
            • medeekM
              medeek
              Wow, interesting video put out just yesterday:
              design.medeek.com
                ajmwd
                @medeek said:
                Version 1.5.6 - 07.16.2020
                • Updated the gable wall module to allow for zero wall height shed walls.
                • Added triple single hung windows to the window module.
                http://design.medeek.com/resources/wallplugin/images/wall_su396_800.jpg
                http://design.medeek.com/resources/wallplugin/images/wall_su398_800.jpg
                Thanks! I just made great use of BOTH of these new features and they worked beautifully. πŸ˜„
                Q: if I wanted to add triple 'picture' (fixed) windows, is that something I could do by adding to the Medeek plugin library folder?
                • medeekM
                  medeek
                  The casement window option is probably what you are looking for:
                  http://design.medeek.com/resources/images/wall_su178_800.jpg
                  design.medeek.com
                    ajmwd
                    @medeek said:
                    The Triple Casement window option is probably what you are looking for...
                    Thanks for the quick response. I didn't think of using the Triple Casement option because we would not actually be ordering casement windows (this is for a set of windows that are very high on the wall and completely inaccessible to operating). However, it does the trick in terms of getting the look. Thanks for the tip!
                    PS. We are going with Andersen 100 Series. For some reason it appears that the picture window frame is significantly larger than the hung sash frame, for some reason? The Triple Casement match the hung frame size, which will be totally fine for our purposes. Thanks for the tip!
                    • medeekM
                      medeek
                      The casement style window is very similar (identical) to the picture style window in geometry. I guess I probably should add an option for multi-picture windows.
                      design.medeek.com
                        ajmwd
                        Thanks. I think I should clarify my statement... I was stating that Andersen shows a different glass size for Picture and Casement at the same window width. However, after reviewing their size chart documents, it appears that was just a perception of mine. Andersen size charts show both Picture and Casement windows have the SAME unobstructed glass size of...
                        Width = window width βˆ’ 6.250".
                        Height = window height βˆ’ 6.250".
                        So the Triple Casement will be totally fine at representing Triple Picture. Thanks for the information and clarification. πŸ˜„
                        • medeekM
                          medeek
                          I wouldn't exactly call this a schedule as much as a CSV or spread sheet with all of the shearwall data contained within it. Regardless here is a first look at the Shearwall Schedule tool (preview menu):
                          https://aws1.discourse-cdn.com/sketchup/original/3X/0/f/0fb7e0842ea61f46c58c353c594b5346c8585d0d.jpeg
                          Note that the preview (or HTML menu) only shows limited information. The CSV output is much more comprehensive, listing all of the parameters for the shearwall (ie. holdowns, anchor bolts, clips, blocking etc...)
                          I still have not ironed out all of the details I want to show or present within this schedule tool so additional feedback will be key as to how this evolves. I will probably dig into my original shearwall calculator and figure out how to best incorporate some engineering into this tool. I think it would be useful for the tool to calculate the shear capacity of the SW given its dimensions, sheathing and nail patterns. I also think additional parameter(s) for the actual applied shear load (wind and seismic) might be useful as well, I will need to give this some more thought.
                          Note that the tool is smart enough to detect if there are windows or doors within the bounds of a shearwall panel and correctly labels it with a "PERF" designation, which signifies it is a perforated shearwall.
                          design.medeek.com
                            ajmwd
                            Wow, this is a bit of a crossover for me. I am VERY familiar with Matt Petrowsky from his EXTENSIVE set of FileMaker database development videos on FileMakerMagazine.com. Very interesting to see that he now also has an interest in SketchUp and particularly Medeek. Pretty cool. πŸ˜„
                            • medeekM
                              medeek
                              An example of the CVS output loaded into Excel:
                              https://aws1.discourse-cdn.com/sketchup/optimized/3X/b/e/be6f5247d992edee9cbb5a51eb9ed97acd4711c9_2_690x281.jpeg
                              Notice that have switched the order of some of the parameters to a more logical order.
                              design.medeek.com
                              • medeekM
                                medeek
                                Version 1.7.8 - 01.03.2021
                                • Added the Shearwall Schedule tool to the SW toolbar.
                                http://design.medeek.com/resources/images/wall_sw_su_menu_active.jpg
                                design.medeek.com
                                • medeekM
                                  medeek
                                  First look at shearwall blocking:
                                  https://aws1.discourse-cdn.com/sketchup/original/3X/1/7/17f54ca6638901684f67308b114974863260975c.jpeg
                                  Note that in this example the blocking has been rotated 90 degrees. The rotation parameter allow for zero or 90 deg. rotation. Also note that any number of rows of blocks can be specified. In this case I had a 12' wall so I went with blocking at 4' and 8' (48,96).
                                  Each shearwall panel can have its own blocking which is independent from other shearwalls and is also independent of any general wall blocking.
                                  design.medeek.com
                                  • medeekM
                                    medeek
                                    Version 1.7.9 - 01.05.2021
                                    • Enabled blocking within the shearwall module.
                                    http://design.medeek.com/resources/wallplugin/images/wall_su454_800.jpg
                                    The blocking module algorithm for shearwalls was a bit more of hassle than I had hoped but after about 16 hours of scratching my head I managed to cobble it together. I'm fairly happy and confident with the results but I am sure there will be a few cases where it may need further refinement. The true debugging process really only starts now as I hand it over to the customer to use in real design situations.
                                    I've beaten the Shearwall "horse" for about a week now (Dec. 27th - Jan. 5th), I do have more engineering work that can be done but I think I will probably give it a rest for a while and move on to other hot items within the Truss plugin.
                                    If you have additional items that you would like to see added to this module please feel free to send me an email. I am much more likely to address follow up items when the programming is still fresh on my mind. A month from now it will take more effort to dig back into the shearwall module and add or improve existing features.
                                    design.medeek.com
                                    • medeekM
                                      medeek
                                      Version 1.7.9b - 01.05.2021
                                      • Added the following Simpson Strong-Tie holdowns to the shearwall module: HTT4, HTT5, HDQ8.
                                      http://design.medeek.com/resources/wallplugin/images/wall_su455_800.jpg
                                      Added per customer request.
                                      design.medeek.com
                                      • medeekM
                                        medeek
                                        Version 1.7.9c - 01.09.2021
                                        • Added the following Simpson Strong-Tie holdowns to the shearwall module: HHDQ11, HHDQ14.
                                        http://design.medeek.com/resources/wallplugin/images/wall_su456_800.jpg
                                        Another customer request.
                                        design.medeek.com
                                        • medeekM
                                          medeek
                                          Version 1.8.0 - 01.16.2021
                                          • Added a "Remove Cladding Lines" option within the global settings.
                                          http://design.medeek.com/resources/wallplugin/images/wall_su457_800.jpg
                                          design.medeek.com
                                          • medeekM
                                            medeek
                                            I've been meaning to add the sliding glass door type for a while but it always seems to get pushed back due to some other priority. So tonight I hammered out the final details and I will work on adding it as an additional door type.
                                            I am using Andersen's 100 series (no flange) sliding glass door as the template. This should provide a fairly universal option for a sliding glass door. More exotic options can always be inserted by the user.
                                            Initially I will disable sidelites and transoms for this door type however I will probably add those options in at a later date as they are requested.
                                            My quick and dirty diagram outlining the dimensions for this door type:
                                            https://aws1.discourse-cdn.com/sketchup/optimized/3X/c/e/cea119c40efc2c6f710ed79ae66a427e94205560_2_386x500.jpeg
                                            design.medeek.com
                                            • 47
                                            • 48
                                            • 49
                                            • 50
                                            • 51
                                            • 80
                                            • 81
                                            • 49 / 81