    This image demonstrates the vertical drop option/parameter along with various rebar configurations:

    http://design.medeek.com/resources/trussplugin/images/truss_su455_800.jpg

    The footing to the far right is a typical 12" deep shallow footing with two bars.

    The two central footings are 18" deep (4" slab) with a 10" vertical drop. When you specify a qty. of four or six bars the plugin will arrange the bars top and bottom as shown otherwise the bars will be positioned at the bottom of the footing (with a 3" ground clearance).

    Note that all of the footings shown have a slope of 45 deg. however this can also be customized to any angle.

    Nathaniel P. Wilkerson PE
    Medeek Engineering Inc
    design.medeek.com

    1 Reply Last reply Reply Quote 0
    • M Offline
      medeek
      last edited by 14 Jul 2019, 01:28

      Working in 3D is a bit different, and poses some additional challenges, when compared with designing in a 2D environment.

      Slab-on-Grade interior footings are an excellent example of this type of problem. In a 3D environment you are usually wanting to work on your model looking down at it rather than looking up at it. Unless you have modified the transparency of concrete material you are typically unable to view the interior footings you have created.

      To remedy this problem I have created a hidden layer (normally hidden) that is toggled on when you go to add, edit, delete or move an interior footing. This layer not only contains the outline of each footing but also the label assigned to each by the plugin:

      http://design.medeek.com/resources/trussplugin/images/truss_su456_800.jpg

      This layer can always be toggled manually by the user, but I have also setup the various tools to toggle it on and off during appropriate actions.

      Nathaniel P. Wilkerson PE
      Medeek Engineering Inc
      design.medeek.com

      1 Reply Last reply Reply Quote 0
      • M Offline
        medeek
        last edited by 14 Jul 2019, 01:46

        As I've been putting the new interior footing module through its paces it occurred to me that the waffle type floor systems seen in large parking structures and in Australian residential construction will now be possible with this new feature.

        I'm pretty excited to finally see this feature become a reality. I should have made this happen a couple years ago, but in all truthfulness I probably did not possess the programming chops or experience to make it happen at the time.

        Fast forward a couple years, and I have much better handle of what I can and can't do with SketchUp's API. I've also been able to lean on and gain advice from some of the SketchUp sages along the way. Thank-you for coming to my rescue, and being so generous with your advice and time, it has made all the difference.

        Nathaniel P. Wilkerson PE
        Medeek Engineering Inc
        design.medeek.com

        1 Reply Last reply Reply Quote 0
        • M Offline
          medeek
          last edited by 14 Jul 2019, 20:34

          Version 1.3.0 - 07.14.2019

          • Added interior footings for rectangular slab-on-grade foundations.
          • Added interior footings for polygon slab-on-grade foundations.
          • Enabled editing, moving and deleting of interior footings for all slab-on-grade foundations.

          http://design.medeek.com/resources/trussplugin/images/truss_su457_800.jpg

          This is a substantial upgrade for slab-on-grade foundations. I've completely removed the old interior footing code and replaced it with the new interior footing module. The ability to add, move, edit and delete each interior footing on an unlimited basis is a breath of fresh air for this plugin.

          Now I just need to do something similar for stemwall foundations and slabs... there is always more to do.

          Later today, after a small break, I will put out a tutorial video explaining the features of this new module and demonstrate its use.

          Nathaniel P. Wilkerson PE
          Medeek Engineering Inc
          design.medeek.com

          1 Reply Last reply Reply Quote 0
          • J Offline
            juju
            last edited by 14 Jul 2019, 21:10

            your download page for this indicates version 1.2.3 released 07/14/2019.

            Save the Earth, it's the only planet with chocolate.

            1 Reply Last reply Reply Quote 0
            • M Offline
              medeek
              last edited by 15 Jul 2019, 01:00

              @juju said:

              your download page for this indicates version 1.2.3 released 07/14/2019.

              Which page are you referring to? Can you give me the URL. The plugin page on my website is showing version 1.3.0.

              Nathaniel P. Wilkerson PE
              Medeek Engineering Inc
              design.medeek.com

              1 Reply Last reply Reply Quote 0
              • M Offline
                medeek
                last edited by 15 Jul 2019, 01:13

                I've been considering the addition of a tool that adds in a depression to the slab-on-grade. The user would create any polygon shape which would then be used to generate this depressed region on the slab.

                The actual modifications to the concrete slab would be fairly easy to accomplish with the API however a number of ripple effects would pose other problems. The first problem would be slab reinforcement. The depressed region would need to have its reinforcement translated down with the slab so it remains centered within the slab.

                A similar problem exists for slab insulation and subbase material, these items would need to be moved down in the z direction as well. This of course is assuming that the slab in the depressed region remains the same thickness as the rest of the slab, however this might not be the case.

                One could assign the a zero thickness to the depressed region slab thickness which essentially cuts a hole in the slab if the depression is equal to the slab thickness.

                Or one could specify a thicker slab in this depressed region.

                Regardless slab depressions are quite interesting and introduce a number of complex problems when combined with other features like internal footings, slab insulation, subbase and slab reinforcement.

                Nathaniel P. Wilkerson PE
                Medeek Engineering Inc
                design.medeek.com

                1 Reply Last reply Reply Quote 0
                • M Offline
                  medeek
                  last edited by 15 Jul 2019, 02:19

                  After mauling this over a bit more I think I can deal with the concrete, slab insulation, interior footings and subbase fairly easily with a slab depression, however the slab reinforcement is a bit more challenging. Even the footing top bars are a bit problematic ( they need to be dropped as well) as one can see in the image below:

                  http://design.medeek.com/resources/trussplugin/images/truss_su458_800.jpg

                  At the moment I don't have a good answer for how to deal with slab depressions when combined with slab reinforcement. If anyone has a good idea I'm open to suggestion.

                  This type of slab depression (4") is fairly typical for a garage that is attached to the main residence.

                  View model here:

                  Link Preview Image
                  3D Warehouse

                  3D Warehouse is a website of searchable, pre-made 3D models that works seamlessly with SketchUp.

                  favicon

                  (3dwarehouse.sketchup.com)

                  I'm not saying there are not solutions to this problem but they become very computationally expensive (ie. boolean subtraction) and are not at all optimal.

                  Nathaniel P. Wilkerson PE
                  Medeek Engineering Inc
                  design.medeek.com

                  1 Reply Last reply Reply Quote 0
                  • J Offline
                    juju
                    last edited by 15 Jul 2019, 10:00

                    @medeek said:

                    @juju said:

                    your download page for this indicates version 1.2.3 released 07/14/2019.

                    Which page are you referring to? Can you give me the URL. The plugin page on my website is showing version 1.3.0.

                    see attached 👍


                    medeek foundation.jpg

                    Save the Earth, it's the only planet with chocolate.

                    1 Reply Last reply Reply Quote 0
                    • M Offline
                      medeek
                      last edited by 15 Jul 2019, 17:11

                      A website typo, please check it now...

                      Thank-you for promptly bringing this to my attention.

                      Nathaniel P. Wilkerson PE
                      Medeek Engineering Inc
                      design.medeek.com

                      1 Reply Last reply Reply Quote 0
                      • M Offline
                        medeek
                        last edited by 15 Jul 2019, 20:19

                        Tutorial 3 - Interior Footings for Slab-on-Grade Foundations (16:33 min.)

                        Interior footings for rectangular slab-on-grade foundations is identical to working with polygon shaped foundations.

                        Nathaniel P. Wilkerson PE
                        Medeek Engineering Inc
                        design.medeek.com

                        1 Reply Last reply Reply Quote 0
                        • M Offline
                          medeek
                          last edited by 15 Jul 2019, 23:59

                          First look at the slab depression toolbar:

                          http://design.medeek.com/resources/images/foundation_dep_su_menu_active.jpg

                          This toolbar will allow the user to add, delete, edit or modify slab depressions within slab-on-grade or slab foundations.

                          Nathaniel P. Wilkerson PE
                          Medeek Engineering Inc
                          design.medeek.com

                          1 Reply Last reply Reply Quote 0
                          • M Offline
                            medeek
                            last edited by 16 Jul 2019, 03:40

                            BUG REPORT: I'm missing a transform in the "Add Interior Footing" tool, so if a foundation is created in a location other than the origin, it may produce an unexpected result (ie. shifted footing location). I am working on the fix currently. Funny that I never exposed this error in my testing or even in the tutorial video, it does take a special set of circumstances.

                            I've also identified another issue where two footings might be coincident at their ends (start or end) at a non-orthogonal angle, see image below:

                            http://design.medeek.com/resources/trussplugin/images/truss_su459_800.jpg

                            In such a situation rather than sloping the ends of the footing towards each other I need to miter the ends so that they meet cleanly. Just some additional code in the block of code that applies the slope to the footings.

                            If three footings or more footings were to meet at a single point then the boolean union of them would work out without a hitch, it is only when you join two footings at their ends that this scenario becomes an issue.

                            Nathaniel P. Wilkerson PE
                            Medeek Engineering Inc
                            design.medeek.com

                            1 Reply Last reply Reply Quote 0
                            • M Offline
                              medeek
                              last edited by 16 Jul 2019, 10:13

                              Version 1.3.0b - 07.16.2019

                              • Added the Slab Depression toolbar and icons.
                              • Enabled a 45 deg. miter option for the ends of interior footings.
                              • Fixed a bug with the initial positioning transforms for the interior footing draw tool.

                              The option for mitering is tucked into the start and end slope option. Now in addition to the Yes/No options you also can have it miter left or right (45 deg only).

                              http://design.medeek.com/resources/trussplugin/images/truss_su460_800.jpg

                              This is a critical update since the transform bug was a significant issue with Version 1.3.0.

                              The slab depression functions/tools are still under construction and currently not functional.

                              Nathaniel P. Wilkerson PE
                              Medeek Engineering Inc
                              design.medeek.com

                              1 Reply Last reply Reply Quote 0
                              • M Offline
                                medeek
                                last edited by 16 Jul 2019, 19:30

                                Hmmm, you might be on to something with this.

                                I agree that the amount of toolbars has multiplied quite rapidly as I keep adding more features to each plugin, it does take up quite a bit of screen real estate now.

                                Nathaniel P. Wilkerson PE
                                Medeek Engineering Inc
                                design.medeek.com

                                1 Reply Last reply Reply Quote 0
                                • J Offline
                                  juju
                                  last edited by 16 Jul 2019, 19:33

                                  thanks for the efforts!

                                  the toolbars for your extensions are becoming rather elaborate and taking up a bit of toolbar / screen space, any chance you could implement a single initiation button/icon instead and have a secondary open when the primary has been triggered, much like Fredo does some of his extensions?

                                  Save the Earth, it's the only planet with chocolate.

                                  1 Reply Last reply Reply Quote 0
                                  • M Offline
                                    medeek
                                    last edited by 19 Jul 2019, 22:56

                                    Version 1.3.1 - 07.19.2019

                                    • Added slab depressions for rectangular and polygon slab-on-grade foundations.
                                    • Enabled editing, moving and deleting of slab depressions for all slab-on-grade foundations.
                                    • When construction callouts and subbase material is enabled, the volume of the subbase material is displayed beneath the foundation label (currently only slab-on-grade foundation assemblies have this feature available).

                                    http://design.medeek.com/resources/trussplugin/images/truss_su461_800.jpg

                                    The slab depression tool can also be used to cut thru holes into the slab, as shown.

                                    Note that additional work still needs to be done to properly modify rebar and mesh for slab depressions. Currently there is no logic in place to modify the perimeter or slab rebar when a slab depression is utilized within a slab-on-grade foundation.

                                    View model here:

                                    Link Preview Image
                                    3D Warehouse

                                    3D Warehouse is a website of searchable, pre-made 3D models that works seamlessly with SketchUp.

                                    favicon

                                    (3dwarehouse.sketchup.com)

                                    Nathaniel P. Wilkerson PE
                                    Medeek Engineering Inc
                                    design.medeek.com

                                    1 Reply Last reply Reply Quote 0
                                    • M Offline
                                      medeek
                                      last edited by 20 Jul 2019, 01:16

                                      Tutorial 4 - Slab Depressions for Slab-on-Grade Foundations (9:35 min.):

                                      View model here:

                                      Link Preview Image
                                      3D Warehouse

                                      3D Warehouse is a website of searchable, pre-made 3D models that works seamlessly with SketchUp.

                                      favicon

                                      (3dwarehouse.sketchup.com)

                                      Nathaniel P. Wilkerson PE
                                      Medeek Engineering Inc
                                      design.medeek.com

                                      1 Reply Last reply Reply Quote 0
                                      • M Offline
                                        medeek
                                        last edited by 21 Jul 2019, 01:41

                                        Trying to take a day off from the programming but my mind keeps coming back to it and the brick ledge module (for slab-on-grade foundations) I have left unfinished.

                                        Giving it a bit of thought this afternoon and I've come up with the following parameters:

                                        • Ledge Width

                                        • Ledge Height

                                        • Start Ext.: Defaults to zero

                                        • End Ext.: Defaults to zero

                                        Really not much to it, or so it would seem.

                                        The idea is to be able to create a brick ledge on any specified edge (perimeter) of the foundation rather than around the entire foundation. A lot of modern designs only utilize a brick facade on the front of the house and not on the rear so this ability to be selective with each wall is critical.

                                        Once I have this feature up and running I think the tools afforded the slab-on-grade type of foundation will allow it to be utilized for most designs however additional work will still need to be done to make the rebar placement correct in a complex design.

                                        Nathaniel P. Wilkerson PE
                                        Medeek Engineering Inc
                                        design.medeek.com

                                        1 Reply Last reply Reply Quote 0
                                        • M Offline
                                          medeek
                                          last edited by 22 Jul 2019, 07:26

                                          First look at brick ledges combined with a slab depression (garage).

                                          http://design.medeek.com/resources/trussplugin/images/truss_su462_800.jpg

                                          The trickiest part of the brick ledge module was the tool that selects the foundation edge. I have it working stably now but I need to add some additional logic which prevents the user from duplicating a brick ledge along the same foundation edge.

                                          I also need to add in some additional logic which offsets the anchor bolts the appropriate amount given the width of the brick ledge.

                                          Similar to the slab depressions the brick ledge module makes no accommodations currently for rebar placement. The logic and algorithms for that will take some considerable effort.

                                          Nathaniel P. Wilkerson PE
                                          Medeek Engineering Inc
                                          design.medeek.com

                                          1 Reply Last reply Reply Quote 0